Figure 2 -- Damper control: Inlet damper requires much less power than outlet damper for the same performance. Basis: motor running at a fixed 1,180 rpm. |
Outlet Dampers. Partially throttled outlet dampers can achieve the desired static pressure and volume at 1,000 BHP (Figure 2). The annual operating cost, therefore, is: (1,000 BHP)(0.746 kW/BHP)(350 days/year)(24 hours/day)($0.05 /kWh) = $313,320.Inlet Dampers. Partially throttled radial inlet dampers can reach the same static pressure and volume at only 700 BHP (Figure 2), cutting the annual cost to: (700 BHP)(0.746 kW/BHP)(350 days/year)(24 hours/day) ($0.05 /kWh) = $219,324.Variable Frequency Drives. Employing a VFD allows achieving the same operating pressure and volume at a fan speed of 840 RPM (Figure 3). The figure shows that this reduction in speed drops the required horsepower to only 450 BHP, which generates an annual operating cost of: (521 BHP)(0.746 kW/BHP)(350 days/year)(24 hours/day)($0.05 /kWh) = $140,994.