Neglect Level Control at Your Peril
This first article in a four-part series examines reset mode tuning issues.
By Cecil L. Smith, Cecil L. Smith, Inc.
2 votes
Text size: - +
The level in a process vessel often isn't viewed as a critical variable to control. Especially in surge vessels, controller performance typically is considered satisfactory if no high- or low-level trips occur. Vessel level's effect on the corporate bottom line usually is nil. So, it's easy to see why vessel level controls receive little attention.
However, neglecting level control carries definite risks. Indeed, loss of level control has contributed to three major industrial accidents (see: "Don't Underestimate Overfilling's Risks").
Processes consist of a collection of unit operations. The various flow streams that interconnect these unit operations propagate variance from one to the next. This variance ideally should diminish as it spreads but the nature of some unit operations actually amplifies it.
Control loops also can amplify variance, either through improper operating objectives or poor tuning. The flow between some unit operations depends upon a level controller's output to a final control element on a flow stream. Two factors make level loops a potential source of variance:
  1.  Variance in any stream in or out of a unit operation leads to variance in vessel level, to which the level controller responds by changing the flow of either an inlet or a discharge stream.
  2.  The inherent nature of level processes complicates controller tuning, especially for integral or reset mode. Excessive reset action (i.e., reset time too short or reset rate too fast) results in a cycle in the flow. In the conservatively tuned level loops applied to surge vessels, the slowly responding controller produces a cycle with a period of hours. This is where level differs from other loops — reducing the controller gain or sensitivity doesn't eliminate the cycle but merely increases its period.
Figure 1 shows a vessel with four feed streams and one product stream. The level controller influences just the discharge stream. The only difference between controlling using a feed stream instead of a discharge stream is directionality (increase-increase versus increase-decrease). In Figure 1 the final control element is a valve but a pump with a variable frequency drive often is a viable, and possibly preferable, alternative.
The controller in Figure 1 translates variations in vessel level to variations in discharge valve opening and, hence, discharge flow. Maintaining level within a given proximity to its set point requires certain changes in discharge flow. Generally, the tighter the level is controlled, the larger the necessary variations in discharge flow.
Now, let's consider some characteristics of a feedback controller:
  • It decreases the variance in the control error by increasing the variance in the controller output, which translates to higher variance in the flow through the final control element.
  • It shifts variance from one variable to another; it doesn't reduce total variance.
  • An improperly tuned feedback controller can significantly raise total variance.
Although instrument technicians often are responsible for tuning level controllers in a plant, propagation of variance is a process issue that's most appropriately addressed by process engineers.
INTEGRATING PROCESSES
Most level processes are integrating/ramp/non-self-regulated, the primary exception being gravity flow applications. When the level controller is on manual, with an integrating process:
  • Vessel level changes at a rate proportional to the imbalance in the material balance (total flow in minus total flow out).
  • Changes in level (and, thus, head) don't affect the discharge flow and, consequently, the imbalance in the material balance.
  • The rate of change in level remains the same as the level increases or decreases.
When the level doesn't directly impact any flow in or out, the dynamic characteristics of the process act as an integrator. The integrator in the reset mode of a controller coupled with an integrator in the process can have adverse consequences.
Starting from an equilibrium state (total flow in equals total flow out), any upset results in a ramp change in level, hence the term "ramp process." If the upset conditions persist, the ramp continues until the level reaches a limiting condition, usually in the form of a high- or low-level process trip. When no control actions are taken, such processes don't seek an equilibrium, hence the term "non-self-regulated process."
Figure 2 illustrates the response in level to an upset to the material balance. When the material balance is closed (imbalance is zero), vessel level is constant. In Figure 2, this is the case prior to time 0. At that point the discharge valve opening is reduced by 10%, which decreases discharge flow and causes level to increase.
All examples we'll discuss pertain to a straight-walled vessel containing a constant density liquid, hence the ramp has a constant slope as in Figure 2. We'll express the level as a percentage of the level measurement span. The response in Figure 2 is for a 12,000-L vessel. The average flow through the vessel is 200 L/min, giving a residence time of 60 min or 1 hr.
A simple characterization of a level process relies on two parameters whose value can be readily obtained from the response in Figure 2:
Process gain, KF. This is the effect of a 10% change in the controller output on the slope of the ramp. From Figure 2, a 10% reduction in the controller output causes the slope of the ramp to change from zero to 0.49%/min. So:
2 votes
Read more about
Featured Sponsor